Hello ,
I have problem with reading registars on modbus tcp.
Problem is :
I use beckhoff plc and start address is 32768 and when i want to read one registar i receive error ( P-ModbusTCP 0002: Illegal Data Address: citanje Line 5 - Uncaught error in sequence)
what I noticed in command/Alert program didnt accept start address.
Here is code and command/Alert:
Anyone has same problem??
Modbus start address reading
in Modbus
Posted
it is solved yestrday, it was problem from plc side. Must be defined start address 0, not 32768.
Anyway, thanks for the help