ADAM4000 units via rs485


thnng

Recommended Posts

HI, I AM NEW TO DAQ FACTORY PRO.... TRYING TO GET THE COMM MONITOR TO TALK TO MY ADAM 4000 UNITS ON 485 NETWORK. WHEN USING WINDOWS HYPER-TERMINAL tx AND rx ALL OK TO EACH ADDRESSABLE UNIT, RETURNING DATA AS REQUESTED. UNABLE TO GET DAQFACTORY MONITOR TO TALK TO UNITS!! :huh:

SUGGESTIONS TRULY WELCOME...

THANKS

Link to comment
Share on other sites

The DAQFactory monitor is designed to handle binary data as well as text data. Hyperterminal is really text only, making it impossible to do binary protocols. As a text terminal, it will generate a carriage return when you hit the enter key. In the DAQFactory monitor, only what you type is sent. Hitting the carriage return simply activates the Send button, and does not add the carriage return character. So, if you want to send out "GIVE ME DATA", you would likely put:

GIVE ME DATA\013

Link to comment
Share on other sites

Thanks for this. Monitor is now sending and receiving.

Now.... Trying to create a poll protocol to get data from the ADAM devices. The monitor syntax used to get data from channel 1 of unit with address 1 is "#01113"

How do I incorporate this into the suggested poll expression example given in the manual:

return(StrToDouble(Poll("D"+chr(13),13)))

?

Thanks in anticipation.

thnng

Link to comment
Share on other sites

Well, first, I typically do not recommend creating user protocols unless you are going to reuse it across multiple documents, and if you do create a user protocol, you should script it as sequences first, then migrate. However, if the protocol is dead simple like the ADAM, and it sounds like you already made some progress, you might continue on it. As to your specific question, the output would be:

"#011" + chr(13)

(the forum often strips backslashes, and I'm assuming there was only one backslash in the monitor syntax)

Link to comment
Share on other sites

  • 3 months later...

HI, I have lots of good data now, but I need to use DaqFactory to control outputs on ADAM4000 units. Having problems getting the syntax correct when setting up I/O types in Protocol Configuration part of Serial device configuration.

The syntax below I use to get data from the AI units, and this works well.

private string dataout = "#09" + DoubleToStr(Channel) + Chr(13)

private string datain = Poll(dataout,13)

return(StrToDouble(Mid(datain,1,10)))

However, what I need to do is to control digital out and Analog out. I am not sure how to write a protocol to do this.

The command for the ADAM module (4150) is:

#AABB

Name Digital Data Out

Description The command either sets a single digital output channel or

sets all digital output channels simultaneously.

Syntax #AABB(data)(cr)

# is a delimiter character.

AA (range 00-FF) represents the 2-character hexadecimal

address for the output.

BB is used to indicate whether a single channel or all the

channels will be set. In the last character of BB also indicates

which channel it is.

1. Writing to all channels (write a byte): both characters

should be equal to zero (BB=00).

2. Writing to a single channel (write a bit): First character

is 1, and the second character indicates channel number,

which can range from 0 to B.

(data) is the hexadecimal representation of the digital output

value(s).

If I use the monitor and enter:

#081201\013

I can turn on channel 2 at address 08.....

Then off with this...

#081200\013

How can I write these into a device I/O protocol and also adapt for use as a toggle on/off switch in DaqFactory?

...

Also, .any help with Analog out would be great (below).

Thanks in anticipation.

S. Thnng

ADAM4024.

#AA

Name Analog Data Out

Description Send a value to the addressed analog output module. Upon

receipt, the analog output module will output this value.

Syntax #AA(data)(cr)

# is a delimiter character.

AA (range 00-FF) represents the 2-character hexadecimal

address of an analog output module.

(data) is the value that has to be output through the analog

output module. Range and value depend on the module’s

configured data format. Possible formats are: engineering

units, % of FSR or hexadecimal.

#AA

Example command: #3315.000(cr)

response: >(cr)

The command sends the value 15 mA to the analog output

module at address 33h that is configured for engineering units.

The analog output module responds that the command was

valid. Its output value will be 15 mA.

Link to comment
Share on other sites

Hi,

FIRSTLY-I CURRENTLY USE DEVICE I/O PROTOCOLS TO READ DATA FROM MY ADAM 4000 UNITS AND USE THE FOLLOWING FUNCTION

private string dataout = "#06" + DoubleToStr(Channel) + Chr(13)

private string datain = Poll(dataout,13)

return(StrToDouble(Mid(datain,1,10)))

THIS WORKS WELL.

HOWEVER; i WOULD LIKE WRITE A PROTOCOL TO SEND DATA (ON/OFF) TO AN ADAM DEVICE USING A PROTOCOL FUNCTION SO THAT I CAN USE THE TOGGLE FEATURE IN A BUTTON.

IS THIS POSSIBLE?

THANKS

THNNG :)

Link to comment
Share on other sites

Depends where you are doing this. It looks like you are doing this in an actual user protocol since you are using the Poll command. If so, you should be able to create a new I/O type, specify that its an output, and then still use the poll() function just like you did before. Typically, however, you'll simply want to return the OriginalValue variable. It might look like this:

private string dataout = "#08" + format("%02X",Channel) + format("%02X", SetToValue) + Chr(13)

private string datain = Poll(dataout,13)

return(originalValue)

Link to comment
Share on other sites

Hi,

Thanks for the reply. Yes I am using user protocols. I tried your suggestion but to no avail.

I also tried:

private string dataout = “#081” + DoubleToStr(Channel) + DoubleToStr(SetToValue) + Chr(13)

private string datain = Poll(dataout,13)

return(originalValue)

//ADAM4000 Syntax

//#AABB

//command: #081201(cr)

//response: >(cr)

//An output bit with value 1 is sent to channel 2 of a digital

//I/O module at address 08h. Channel two of the digital I/O

//module is set to ON.

Still no joy...... :mellow:

Link to comment
Share on other sites

This might help:

#AABB

Name Digital Data Out

Description The command either sets a single digital output channel or

sets all digital output channels simultaneously.

Syntax #AABB(data)(cr)

# is a delimiter character.

AA (range 00-FF) represents the 2-character hexadecimal

address for the output.

BB is used to indicate whether a single channel or all the

channels will be set. In the last character of BB also indicates

which channel it is.

1. Writing to all channels (write a byte): both characters

should be equal to zero (BB=00).

2. Writing to a single channel (write a bit): First character

is 1, and the second character indicates channel number,

which can range from 0 to B.

(data) is the hexadecimal representation of the digital output

value(s).

:)Thanks in anticipation.

Link to comment
Share on other sites

Drop the 1, and you have to use the format() not doubleToStr() to ensure you have two characters:

private string dataout = "#08" + format("%02X",Channel) + format("%02X", SetToValue) + Chr(13)

I'm assuming the address is 08.

Link to comment
Share on other sites

You might consider replacing the 08 with deviceNumber:

private string dataout = "#" + format("%02X",deviceNumber) + format("%02X",Channel) + format("%02X", SetToValue) + Chr(13)

Then you can fully specify the channel details right in the channel table. The ID would be the D# of the channel.

Link to comment