kanber Posted August 17, 2015 Share Posted August 17, 2015 Hi, I tried to configuration to daqfactory as modbus slave. But I test with your advanded modbus tool. In master Tx is looking clear. But when I open in slave it is not clear. Please see attached file. Link to comment Share on other sites More sharing options...
AzeoTech Posted August 18, 2015 Share Posted August 18, 2015 Sorry, nothing was attached. Also, what release of DAQFactory are you running and what version? Link to comment Share on other sites More sharing options...
kanber Posted August 19, 2015 Author Share Posted August 19, 2015 I am using 5.79. I attached file Link to comment Share on other sites More sharing options...
AzeoTech Posted August 20, 2015 Share Posted August 20, 2015 Upgrade to 5.87, or 5.9+. I can't readily address issues with a release that is many years old. Link to comment Share on other sites More sharing options...
kanber Posted August 26, 2015 Author Share Posted August 26, 2015 I tried with 5.87c. it is also same. what can it be? Is there any master and slave template runtime to check and see how it is done. Link to comment Share on other sites More sharing options...
AzeoTech Posted September 1, 2015 Share Posted September 1, 2015 What version of DAQFactory are you using? Slave is only supported in Pro. To create a slave, go to the new serial/ethernet device configuration. Create a new serial port or ethernet server. Select either ModbusTCP slave or ModbusRTU slave and give the device a name. You will NOT use this name in any channels. To assign a channel to be accessible by the Modbus slave driver, go to the Mod Slave # column and enter a tag number between 1 and 9999 for an integer, and 10000 and 19999 for a float. The modbus ID is 1, though this can be changed in script. Link to comment Share on other sites More sharing options...
kanber Posted October 12, 2015 Author Share Posted October 12, 2015 Hi, I am still trying to connect to daqfactory as a slave. I make the program and from another computer with advanded modbus scanner I tested and it is worked. and data format like below, Daqfactory Tx: \000\000\000\000\000\005\255\003\002\000\190 Rx: \001\000\000\000\000\000\006\255\003\000\001\000 Tx: \000\000\000\000\000\005\255\003\002\000\190 Rx: \001\000\000\000\000\000\006\255\003\000\001\000 Then I add the point aother program and data is below; Rx: _ Rx: \145 Rx: \000 Rx: \000\000\006\255\003 Rx: \000\001\000 Tx: _\145\000\000\000\005\255\003\002\000\160 Rx: \001_\146\000\000\000\006\255\003\000\001\000 Tx: _\146\000\000\000\005\255\003\002\000\160 Rx: \001_\147\000\000\000\006\255\003\000\001\000 Tx: _\147\000\000\000\005\255\003\002\000\160 Rx: \001_\148\000\000\000\006\255\003\000\001\000 Tx: _\148\000\000\000\005\255\003\002\000\160 Rx: \001 Rx: _ Rx: \149\000 Rx: \000\000\006 Rx: \255 Rx: \003 Rx: \000 Rx: \001 Rx: \000 Tx: _\149\000\000\000\005\255\003\002\000\160 Rx: \001_\150\000\000\000\006\255\003\000\001\000 Tx: _\150\000\000\000\005\255\003\002\000\160 Rx: \001_\151\000\000\000\006\255\003\000\001\000 Tx: _\151\000\000\000\005\255\003\002\000\160 Rx: \001_\152\000\000\000\006\255\003\000\001\000 Tx: _\152\000\000\000\005\255\003\002\000\160 Rx: \001 Rx: _ Rx: \153 Rx: \000\000 What is the problem or reason? NOTE: I am using 5.87c. And I attached slave parameters also. Link to comment Share on other sites More sharing options...
AzeoTech Posted October 12, 2015 Share Posted October 12, 2015 First, when viewing binary protocols in the monitor, make sure "Display all chars as ASCII codes" is checked, otherwise you get a mix of numbers and characters like, in your case, the underscore. That said, the protocol stream appears to be functioning. My only comment is that you really shouldn't use Modbus ID 255. Technically it should be between 1 and 247 inclusive. But with TCP most devices don't care, and certainly DAQFactory doesn't. What is the issue? Are you not seeing values in your other program? Link to comment Share on other sites More sharing options...
kanber Posted October 13, 2015 Author Share Posted October 13, 2015 When data is like that; Tx: _\145\000\000\000\005\255\003\002\000\160 Rx: \001_\146\000\000\000\006\255\003\000\001\000 Tx: _\146\000\000\000\005\255\003\002\000\160 Rx: \001_\147\000\000\000\006\255\003\000\001\000 Tx: _\147\000\000\000\005\255\003\002\000\160 Rx: \001_\148\000\000\000\006\255\003\000\001\000 Tx: _\148\000\000\000\005\255\003\002\000\160 comminication is OK. and RX and TX showing every one second new row when it start to take data like; Rx: \001 Rx: _ Rx: \149\000 Rx: \000\000\006 Rx: \255 Rx: \003 Rx: \000 Rx: \001 Rx: \000 There is no TX because RX is not completed. Daqfactory waiting request. and here every new row coming 3-4 seconds. it takes 25-30 seconds to take all data and other program getting timeout and comminication errors. Link to comment Share on other sites More sharing options...
AzeoTech Posted October 13, 2015 Share Posted October 13, 2015 Actually, the packet is complete. The \001 at the top is actually the last byte of the previous packet, not the first byte of this packet. You can tell because the \006 is the last byte of the TCP header which says "6 bytes coming in the main packet". I would do a few things: 1) as I mentioned, have it show chars as ASCII codes. 2) tell it to display the time of Tx/Rx so you can have a better feel for the timing of these queries. Link to comment Share on other sites More sharing options...
kanber Posted November 14, 2015 Author Share Posted November 14, 2015 Rx (13:41:07.606): \255\003\000\002\000 Tx (13:41:07.808): \001\221\000\000\000\005\255\003\002\000\211 Rx (13:41:07.808): \001\001\222\000\000\000\006\255\003\000\002\000 Tx (13:41:08.058): \001\222\000\000\000\005\255\003\002\000\211 Rx (13:41:08.058): \001\001\223\000\000\000\006\255\003\000\002\000 Tx (13:41:08.261): \001\223\000\000\000\005\255\003\002\000\211 Rx (13:41:08.261): \001\001\224\000\000\000\006\255\003\000\002\000 Tx (13:41:08.458): \001\224\000\000\000\005\255\003\002\000\211 Rx (13:41:08.458): \001\001\225\000\000\000\006\255\003\000\002\000 Tx (13:41:08.589): \001\225\000\000\000\005\255\003\002\000\211 Rx (13:41:08.589): \001\001\226\000\000\000\006\255\003\000\002\000 Tx (13:41:08.859): \001\226\000\000\000\005\255\003\002\000\211 Rx (13:41:08.859): \001\001\227\000\000\000\006\255\003\000\002\000 Tx (13:41:09.070): \001\227\000\000\000\005\255\003\002\000\211 Rx (13:41:09.090): \001\001\228\000\000\000\006\255\003\000\002\000 Tx (13:41:09.374): \001\228\000\000\000\005\255\003\002\000\211 Rx (13:41:09.374): \001\001\229\000\000\000\006\255\003\000\002\000 Tx (13:41:09.589): \001\229\000\000\000\005\255\003\002\000\211 Rx (13:41:09.589): \001\001\230\000\000\000\006\255\003\000\002\000 Tx (13:41:09.792): \001\230\000\000\000\005\255\003\002\000\211 Rx (13:41:09.792): \001\001\231\000\000\000\006\255\003\000\002\000 Tx (13:41:09.989): \001\231\000\000\000\005\255\003\002\000\211 Rx (13:41:09.989): \001\001\232\000\000\000\006\255\003\000\002\000 Tx (13:41:10.190): \001\232\000\000\000\005\255\003\002\000\211 Rx (13:41:10.190): \001\001\233\000\000\000\006\255\003\000\002\000 Tx (13:41:10.390): \001\233\000\000\000\005\255\003\002\000\211 Rx (13:41:10.390): \001\001\234\000\000\000\006\255\003\000\002\000 Tx (13:41:10.589): \001\234\000\000\000\005\255\003\002\000\211 Rx (13:41:10.590): \001\001\235\000\000\000\006\255\003\000\002\000 Tx (13:41:10.787): \001\235\000\000\000\005\255\003\002\000\211 Rx (13:41:10.787): \001\001\236\000\000\000\006\255\003\000\002\000 Tx (13:41:10.989): \001\236\000\000\000\005\255\003\002\000\211 Rx (13:41:10.989): \001\001\237\000\000\000\006\255\003\000\002\000 Tx (13:41:11.189): \001\237\000\000\000\005\255\003\002\000\211 Rx (13:41:11.189): \001\001\238\000\000\000\006\255\003\000\002\000 Tx (13:41:11.387): \001\238\000\000\000\005\255\003\002\000\211 Rx (13:41:11.387): \001\001\239\000\000\000\006\255\003\000\002\000 Tx (13:41:11.590): \001\239\000\000\000\005\255\003\002\000\211 Rx (13:41:11.591): \001\001\240\000\000\000\006\255\003\000\002\000 Tx (13:41:11.790): \001\240\000\000\000\005\255\003\002\000\213 Rx (13:41:11.790): \001\001\241\000\000\000\006\255\003\000\002\000 Tx (13:41:12.038): \001\241\000\000\000\005\255\003\002\000\213 Rx (13:41:12.038): \001\001\242\000\000\000\006\255\003\000\002\000 Tx (13:41:12.239): \001\242\000\000\000\005\255\003\002\000\213 Rx (13:41:12.240): \001\001\243\000\000\000\006\255\003\000\002\000 Tx (13:41:12.540): \001\243\000\000\000\005\255\003\002\000\213 Rx (13:41:12.540): \001\001\244\000\000\000\006\255\003\000\002\000 Tx (13:41:12.734): \001\244\000\000\000\005\255\003\002\000\213 Rx (13:41:12.734): \001\001\245\000\000\000\006\255\003\000\002\000 Tx (13:41:12.935): \001\245\000\000\000\005\255\003\002\000\213 Rx (13:41:12.935): \001 Rx (13:41:32.162): \001\246\000\000\000\006\255\003\000\002\000 Tx (13:41:32.363): \001\246\000\000\000\005\255\003\002\000\211 Rx (13:41:32.363): \001 Rx (13:42:01.592): \001\247\000\000\000\006\255\003\000\002\000 Tx (13:42:01.797): \001\247\000\000\000\005\255\003\002\000\204 Rx (13:42:01.797): \001 Rx (13:42:37.495): \001\248\000\000\000\006\255\003\000\002\000 Tx (13:42:37.696): \001\248\000\000\000\005\255\003\002\000\202 Rx (13:42:37.696): \001\001\249\000\000\000\006\255\003\000\002\000 Tx (13:42:37.897): \001\249\000\000\000\005\255\003\002\000\202 Rx (13:42:37.898): \001 Rx (13:43:09.418): \001\250\000\000\000\006\255\003\000\002\000 Tx (13:43:09.621): \001\250\000\000\000\005\255\003\002\000\209 Rx (13:43:09.621): \001 Rx (13:43:31.666): \001\251\000\000\000\006\255\003\000\002\000 Tx (13:43:31.869): \001\251\000\000\000\005\255\003\002\000\216 Rx (13:43:31.869): \001\001\252\000\000\000\006\255\003\000\002\000 Tx (13:43:31.935): \001\252\000\000\000\005\255\003\002\000\216 Rx (13:43:31.935): \001\001\253\000\000\000\006\255\003\000\002\000 Tx (13:43:32.139): \001\253\000\000\000\005\255\003\002\000\216 Rx (13:43:32.139): \001 Rx (13:43:41.528): \001\254\000\000\000\006\255\003\000\002\000 Tx (13:43:41.727): \001\254\000\000\000\005\255\003\002\000\218 Rx (13:43:41.727): \001 Rx (13:43:42.858): \001\255\000\000\000\006\255\003\000\002\000 Tx (13:43:43.057): \001\255\000\000\000\005\255\003\002\000\218 Rx (13:43:43.057): \001 Rx (13:44:20.805): \002\000\000\000\000\006\255\003\000\002\000 Tx (13:44:21.005): \002\000\000\000\000\005\255\003\002\000\211 Rx (13:44:21.005): \001\002\001\000\000\000\006\255\003\000\002\000 Tx (13:44:21.215): \002\001\000\000\000\005\255\003\002\000\211 Rx (13:44:21.215): \001\002\002\000\000\000\006\255\003\000\002\000 Tx (13:44:21.336): \002\002\000\000\000\005\255\003\002\000\211 Rx (13:44:21.336): \001\002\003\000\000\000\006\255\003\000\002\000 Tx (13:44:21.537): \002\003\000\000\000\005\255\003\002\000\211 Rx (13:44:21.538): \001 Link to comment Share on other sites More sharing options...
AzeoTech Posted November 16, 2015 Share Posted November 16, 2015 Looks like it is working to me. Its returning a value of 211, or occasionally 218. Link to comment Share on other sites More sharing options...
kanber Posted January 9, 2016 Author Share Posted January 9, 2016 Hi, I still have timeout ptoblem with DF. I make test with your "QuickModPro.ctl" as a master. and my program as a slave. I add picture configurations and rx-tx data. But some times master sent tx and on slave nothing. and 45-50 seconds it start to take value again. Where is the problem Link to comment Share on other sites More sharing options...
AzeoTech Posted January 9, 2016 Share Posted January 9, 2016 Sorry, your pictures did not post. Does the system Tx during the 45 seconds with no Rx or is there just no comms traffic for 45 seconds? What is your timeout set to? Are you on an Ethernet or serial connection? Link to comment Share on other sites More sharing options...
kanber Posted January 9, 2016 Author Share Posted January 9, 2016 Master; Tx (15:13:55.226): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:00.273): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:05.321): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:10.398): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:15.448): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:20.484): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:25.550): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:30.618): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:35.655): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:40.682): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:45.720): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:14:50.767): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:14:53.942): \000\000\000\000\000\005\255\003\002\000n Tx (15:14:53.951): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:14:53.955): \000\000\000\000\000\005\255\003\002\000n Tx (15:14:53.961): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:14:53.961): \000\000\000\000\000\005\255\003\002\000n Tx (15:14:54.011): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:14:54.012): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:54.213): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:54.412): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:54.612): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:54.814): \000\000\000\000\000\005\255\003\002\000n Tx (15:14:55.012): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:14:55.013): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:55.214): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:55.413): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:55.614): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:55.814): \000\000\000\000\000\005\255\003\002\000n Tx (15:14:56.004): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:14:56.004): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:56.206): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:56.421): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:56.622): \000\000\000\000\000\005\255\003\002\000n Rx (15:14:56.915): \000\000\000\000\000\005\255\003\002\000n Tx (15:14:57.005): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:14:57.005): \000\000\000\000\000\005\255\003\002\000n Tx (15:14:58.006): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:15:01.246): \000\000\000\000\000\005\255\003\002\000n Tx (15:15:01.251): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:15:01.252): \000\000\000\000\000\005\255\003\002\000n Tx (15:15:01.261): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:15:01.262): \000\000\000\000\000\005\255\003\002\000n Tx (15:15:01.302): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:15:01.303): \000\000\000\000\000\005\255\003\002\000n Tx (15:15:02.013): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:07.079): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:12.137): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:17.175): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:22.202): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:27.229): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:32.256): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:37.294): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:42.360): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:47.407): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:52.446): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:15:57.482): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:02.512): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:07.546): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:12.595): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:17.632): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:22.688): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:27.747): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.318): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.329): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.329): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.339): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.342): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.349): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.350): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.363): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.364): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.374): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.375): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.379): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.380): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.390): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.391): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.399): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.400): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.420): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.421): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:30.429): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:30.430): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:30.721): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:30.934): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:31.011): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:31.011): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:31.241): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:31.449): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:31.731): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:31.933): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:32.011): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:32.012): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:32.242): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:32.444): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:32.663): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:32.873): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:33.003): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:33.003): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:33.289): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:33.584): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:33.785): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:33.985): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:34.005): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:16:34.006): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:34.296): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:34.496): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:34.697): \000\000\000\000\000\005\255\003\002\000n Tx (15:16:35.007): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:40.074): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:45.131): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:50.218): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:16:55.255): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:00.332): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:05.460): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:10.537): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:15.576): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:20.641): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:25.699): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:30.746): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:35.843): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:17:36.991): \000\000\000\000\000\005\255\003\002\000n Tx (15:17:37.005): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:17:37.006): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:37.206): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:37.406): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:37.617): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:37.817): \000\000\000\000\000\005\255\003\002\000n Tx (15:17:38.006): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:17:38.007): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:38.207): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:38.408): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:38.599): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:38.818): \000\000\000\000\000\005\255\003\002\000n Tx (15:17:39.008): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:17:39.008): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:39.220): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:39.431): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:39.631): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:39.830): \000\000\000\000\000\005\255\003\002\000n Tx (15:17:40.011): \000\000\000\000\000\006\255\003\000\001\000\001 Rx (15:17:40.011): \000\000\000\000\000\005\255\003\002\000n Tx (15:17:41.012): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:46.039): \000\000\000\000\000\006\255\003\000\001\000\001 Tx (15:17:51.096): \000\000\000\000\000\006\255\003\000\001\000\001 SLAVE; 0\006\255\003\000\001\000 Tx (15:16:51.490): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:51.490): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:51.501): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:51.501): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:51.506): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:51.506): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:51.516): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:51.516): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:51.526): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:51.526): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:51.547): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:51.547): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:51.556): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:51.556): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:51.847): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:51.847): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:52.061): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:52.061): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:52.137): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:52.137): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:52.367): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:52.367): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:52.576): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:52.576): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:52.858): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:52.858): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:53.059): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:53.059): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:53.138): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:53.138): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:53.368): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:53.368): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:53.570): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:53.570): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:53.789): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:53.789): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:53.000): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:53.000): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:54.129): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:54.129): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:54.415): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:54.415): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:54.710): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:54.710): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:54.910): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:54.911): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:55.111): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:55.111): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:55.132): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:55.132): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:55.421): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:55.421): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:55.622): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:55.622): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:55.822): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:55.822): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:16:56.022): \000\000\000\000\000\005\255\003\002\000n Rx (15:16:56.022): \001 Rx (15:17:58.117): \000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:58.132): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:58.132): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:58.332): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:58.332): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:58.533): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:58.533): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:58.743): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:58.743): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:58.944): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:58.944): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:59.133): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:59.133): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:59.334): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:59.334): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:59.533): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:59.533): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:59.725): \000\000\000\000\000\005\255\003\002\000n Rx (15:17:59.725): \001\000\000\000\000\000\006\255\003\000\001\000 Tx (15:17:59.944): \000\000\000\000\000\005\255\003\002\000n Link to comment Share on other sites More sharing options...
Recommended Posts
Archived
This topic is now archived and is closed to further replies.