I'm working on a facilities monitoring installation... I need to alarm if LAN cables (Modbus TCP) are disconnected.

I have one set of channels (the Click PLC) being polled in a sequence.  I can try-catch a timeout and flag this error... but the sequence bombs and has to be restarted after the cable is re-plugged.  At least I know there's a problem.

The other set of channels (the H2 generator) is polled by the normal channel-device loop.  I've tried comparing GetTime(mychan[0]) == GetTime(mychan[2]) and it seems that the channel is not updated when a timeout occurs... which I fully support as normal.

Is there a graceful way to set an alarm on a channel timeout?  Is there a way to catch a timeout and spin until the read is made OK, without bombing the sequence?  TIA.

Share this post


Link to post
Share on other sites

The sequence shouldn't bomb out if you use a proper try/catch.  If it is then you might have it setup wrong.  Post your script.

If you are using channel timing, then you'll need to use the other method that you used in H2 generator, but slightly different.  Comparing mychan[0] to time of mychan[2] doesn't really help unless your code is updating mychan with the same timestamp.  I prefer to calculate data age using systime(), for example:

systime() - getTime(myChan[0]) > 10

which will return true if myChan hasn't been updated in 10 seconds.

Share this post


Link to post
Share on other sites
21 hours ago, AzeoTech said:

> The sequence shouldn't bomb out if

> you use a proper try/catch.  If it is then

> you might have it setup > wrong.  Post your script.

<>

while(1)
   
lamp_update()

delay(0.1)

private In0

try
   In0 = Device.ClickDevice.ReadCoilStatus(0,0xF066,1)
catch()
   Click_PLC_Comm_Alm = 1
endcatch

env_CommErr.AddValue(In0[0][0])


delay(0.1)

private In = Device.ClickDevice.ReadHoldingS32(0,10,4)

etc etc...

</>

So ideally I'd like to spin on that first read until the device comes back... there is a device Write() in LampUpdate(), but it doesn't seem to cause an alarm.  I tried putting a 'contine' inside the catch but that didn't help.

 

Thanks for your help, the other solution is elegant (for the H2) and I understand how to implement it.

Share this post


Link to post
Share on other sites

The problem is that you only have that one query inside a try/catch.

What I often do is create stub functions for comms.  So instead of calling device.ClickDevice.ReadCoilStatus() status directly, you'd create a function called, say "ClickReadCoilStatus()" that would take the required parameters, probably just address and num values, and call device.ClickDevice.ReadCoilStatus() in there inside a try / catch:

function clickReadCoilStatus(address, num)

   try
      private ret = device.clickDevice.ReadCoilStatus(0, address, num)
      return(ret)
   catch()
      ? strLastError
      Click_PLC_Comm_Alm = 1
   endcatch
   return(-1)

The only problem is you still have to check the result in your core program, as it returns -1 to indicate failure, but at least it won't crash out of the calling sequence. 

The other option is to put a try/catch around the entire contents of the while() except the delay:
 

while(1)
   try
      lamp_update()
      delay(0.1)
      // .... etc....
   catch()
       ? strLastError
      Click_PLC_Comm_Alm = 1      
   endcatch
   delay(0.1)
endwhile

You have to have a delay outside the loop, or in the catch() so that if you get constant errors from programming fault instead of comms you don't end up with an infinite loop without a delay(), which will tie up the CPU.
       
 Also note that using 0 for the Modbus ID is invalid, even in ModbusTCP.  An ID of 0 indicates "broadcast" in Modbus, which means that any device on the chain may respond.  With ModbusTCP there usually isn't a chain, and often TCP devices just ignore the ID, but still, you should use a valid ID so that you don't screw yourself if you change hardware, or they do a firmware update that changes the behavior of the device to only accept valid IDs.  It is also just good form.

 

 