julius228 Posted June 17, 2008 Share Posted June 17, 2008 Dear all, What I am tring to do is to delete the channel history of a long list of channel by a sequence and I was wondering if is possible to access the channel function using a string reference. I try to explain better whit some code: Private string ChListStr = Channel.ListAll("Main") //List of all channell var.CntDel //counter While(CntDel<=NumRows(ChListStr)) ChListStr[CntDel].ClearHistory() CntDel++ EndWhile I tried to execute this, but doesn't work Any suggestion? Hope to make clear myself, thanks Link to comment Share on other sites More sharing options...
AzeoTech Posted June 17, 2008 Share Posted June 17, 2008 There are several problems: 1) the line: var.CntDel // counter does nothing. Use the new declaration and make sure and initialize CntDel: private CntDel = 0 2) You never initialize CntDel, so the rest won't really work. For() loops are often better for this sort of thing than while: for (private cntdel = 0, cntdel < NumRows(ChListStr), cntdel++) ... endfor 3) you want to do < NumRows(), not <= NumRows(). DAQFactory, like just about every other programming language, indexes everything from 0, so if you have 5 rows, they'll be numbered 0,1,2,3,4. So you pretty much always want < because there is no row 5. 4) ChListStr is an array of strings, not objects, so you can't do: ChListStr[CntDel].ClearHistory() you need to use the execute() function: execute(ChListStr[CntDel] + ".ClearHistory()") Change all that and it should work. Here is the final: Private string ChListStr = Channel.ListAll("Main") //List of all channell for (private cntdel = 0, cntdel < NumRows(ChListStr), cntdel++) execute(ChListStr[CntDel] + ".ClearHistory()") endfor Link to comment Share on other sites More sharing options...
julius228 Posted June 18, 2008 Author Share Posted June 18, 2008 I was confused how to use variable and I completely ignored the execute command. Now everything is clear. Thank you very much for the fast and clear help. Giulio Link to comment Share on other sites More sharing options...
ekanderson Posted May 8, 2009 Share Posted May 8, 2009 I'm using about the same code with exception of using () around channel instead of [] Almost all channels have history lengths of 240, persist of 240. for next loop execute(channel_list(c_c) +".clearHistory()") delay(2) execute("V." +channel_list(c_c) +".clearHistory()") delay(2) next Before I added the delays, channel clearing was hit or miss. After adding delays, ----- All channels routinely clear, except Real channel_list(5) and (8), sometimes (8) clears. Sometimes all channels clear. channels 5 and 8 are named "nHum" and "nVsup" respectively. Another channel has name of "nBar" and clears correctly. Upping the delays to 3 hasn't seemed to help. Going up further, will cause a ripple affect on the amount of code that would have to be revised. Any suggestions??????? on what to look for.?????? ek Link to comment Share on other sites More sharing options...
AzeoTech Posted May 11, 2009 Share Posted May 11, 2009 Why are you using (). Is channel_list a function? Also I'm assuming you actually have a properly formatted for loop and didn't start in on another language that uses for next loop / next. To help further I need more detail on what channel_list is. I would also consider adding a ? statement before each execute() that displays what is executing, so: ? channel_list(c_c) + "clearHistory()" Link to comment Share on other sites More sharing options...
ekanderson Posted May 11, 2009 Share Posted May 11, 2009 Here's modified code as run just now replace channel_list() with channel_list[] ****************** // new way of doing weather Modified 11 May 09 // 18 Feb 09 set up // 28 Apr 09 add one to max(chan_count, V_chan_count) // 01 May 09 add PersitAmount =0 and PersistAmount =Pa() // 03 May 09 eka Read the fine print. Have to do Channel.Restart() // added "V." for Virtual channels // 08 May 09 eka delay from 2, to 3 between clears // 11 May 09 eka use [] instead of () in Channel_list[] // function clear_all_histories() // Chan_list() MUST have been called to set our vars // private c_c =0 // channel loop counter private Pa // added 01 May 09 private string PaS // added 01 May 09 // most channels we have to do // added 1 to it 28 Apr 09 private c_l =max((chan_count, V_chan_count)) +1 private string base_time =doubletostr(R_count_last_time) // read current Persist, set to 0, clear history for (c_c =0, c_c <=c_l, c_c++) if (c_c <=chan_count) ? c_c // debug ? 'execute(channel_list[c_c] +".clearHistory()")' execute(channel_list[c_c] +".clearHistory()") // don't ask me why, but needs [] rather than () // execute("Pa[c_c] =" +channel_list(c_c) +".PersistAmount") // 01 May 09 // execute(channel_list(c_c) +".PersistAmount =0") // 01 May 09 //Channel.Restart() delay(4) // ? Pa[c_c] // debug endif // clear ND also, since we need correct times 18 Feb 09 if (c_c <=V_chan_count) // corrected missing "V." 28 Apr 09 execute("V." +V_channel_list[c_c] +".clearHistory()") delay(4) endif endfor //<<<<<<< end channel loop //nVsup.ClearHistory() //nhum.ClearHistory() //delay(3) ****************************** The above modified code gives SAME results. "nHum" and "nVsup" did not clear. DF 5.80 Here's the ? statement for channel_list *********************** ? channel_list {"Temp_K", "Si_Solar", "Se_Blu", "Se_Grn", "Se_Red", "nHum", "iTemp_F", "nBar", "nVsup", "W_dir", "W_count", "R_count"} ************************ As to () rather than []: 30 years of using () for subscripted vars is my only excuse. ek Link to comment Share on other sites More sharing options...
AzeoTech Posted May 12, 2009 Share Posted May 12, 2009 I didn't think the () would make a difference, I just wasn't sure if you were using it to subset or to call a function. DF actually will accept () for subsetting, but that is not guaranteed to continue, and doesn't always work. Its much cleaner to use a different delimiter []. Anyhow, two things: 1) doing max((chan_count, V_chan_count)) isn't giving you what you think. Its always going to return chan_count. max() takes a single variable, which presumably is an array. What you want is: max(concat(chan_count,V_chan_count)) the concat() function takes the two scalars and makes them into a 2 element array. 2) I'd actually like to see a ? of: ? channel_list[c_c] +".clearHistory()" This will tell us exactly what is getting fed to the execute() function. Then you can try manually typing the line into the command alert for the channels that appear not to work. I assume that absolutely nothing happens to these channels? Link to comment Share on other sites More sharing options...
ekanderson Posted May 12, 2009 Share Posted May 12, 2009 ****** ? channel_list[] +".clearHistory()" {"Temp_K.clearHistory()", "Si_Solar.clearHistory()", "Se_Blu.clearHistory()", "Se_Grn.clearHistory()", "Se_Red.clearHistory()", "nHum.clearHistory()", "iTemp_F.clearHistory()", "nBar.clearHistory()", "nVsup.clearHistory()", "W_dir.clearHistory()", "W_count.clearHistory()", "R_count.clearHistory()"} ******* re max((x,y)) ? max((chan_count, V_chan_count)) 14 ? chan_count 11 ? V_chan_count 14 so that construct does return correct values. I think the double (( )) makes it an array???? with two elements. ***** add_val ="NaN()," if (c_c <=chan_count) execute(channel_list(c_c) + ".addvalue(inserttime(" +add_val +base_time +",0))") endif Above code executes faultlessly (at least for now) in the sequence that "calls" clear_all_histories(). It is in a loop that mirrors the clear history code, but is executed AFTER clearHistory execution. // check_time_lapse() called by cold_start Last modified 12 May 09 //************* should only be called if dp >0 ????? // // 10 Feb 09 eka New approach to starting Weather data collection // check_time lapse will find out time of last measurement // Saves R_count value // fill missing data points with "ND" or NaN, until next measurement time // if greater than 1 day has passed, // Figure out how to check if histories have been exported xxxx // then clear ALL histories. // sets global var dp to appropriate value // 11 Feb 09 eka max((x,y)) add parenthses, singles don't work // moved chan_list() call to cold_start_new // revised how we handle rain_count // 12 Feb 09 Got so didn't bomb // 21 Feb 09 Add some notes on what to do. xxxx // 01 Mar 09 clean up abit // 07 Mar 09 modified if >24 hours logic. Priority to 5 rather than 3, since we want fast // add change day ftp beginseq // Revise for next loop, so add value is Outer loop and channel # is inner // should be more efficent // 20 Mar 09 eka Comment out all code except Rain stuff // 23 Apr 09 eka Try to get to work correctly // Rather than execute, use hard code channel names. // 24 Apr 09 eka Corrected add_date_value to STRING // Found out date add value has to be quoted // 27 Apr 09 eka Revised for Day_changed flag // Remove all date_time channel stuff // 28 Apr 09 eka Correct typo for Day_changed // Revise to do it even if no history // Save and restore some additional channel info // Implement clear_all_histories if Midnite is base time // 29 Apr 09 eka Clear V.R_inches counter // if midnite, add limit to floor // Add 25 seconds to time base just in case // Add msg if clearing histories // Add aHistory export stuff // 01 May 09 eka revise so day_changed valid even if add_lim =0 // Drop R_date_time and Virtual Date_time assignments // 02 May 09 eka Add provision for update of hour xport files // 08 May 09 eka Recalc now time if clear_all_his* done. // Clear R_day_inches if new day // Retry readable Date_time assignment to V channel // 12 May 09 eka Try a clean up of how we do Saves to [0] rather than max[] // Disable Date Time channel execute in channel fill // // *************** MUST save V.R_S_T************** // // Need to modify so can do it if NO history ***** // function check_time_lapse() // DONE in cold_start_new AutoStart Routine find out if we have any history //global dp =numrows(R_count[]) // declare our variables, and set to 0 in case no Histories // 28 Apr 09 Private R_count_save =0 Private R_day_inches =0 Private S_kw_hrs_save =0 Private Rain_Season_total =0 // add for hourly update of xport files 02 May 09 Private string hr Private base_timef Private now_time =floor(systime()) // number of seconds private midnite =floor(systime() /86400) *86400 Global add_lim =floor((now_time -midnite) /360) // to global 28 Apr 09 global R_count_last_time =midnite if (dp >0) // now if have History set these 28 Apr 09 // moved up to here 12 Feb 09, make global for other sequences 18 Feb 09 // add 360 25 Apr 09 // add 25 seconds, just in case it was slow 29 Apr 09 R_count_last_time =(floor((R_count.Time[0] +25) /360) *360) +360 // save our last time // we have SOME history // so save R_count[0] // Save more stuff 28 Apr 09 R_count_save =R_count[0] // use only if LJ_reset_done =0 R_day_inches =V.R_d_inches[0] // [0] rather than max [] S_kw_hrs_save =V.S_kw_hrs[0] // ditto // end save more stuff 28 Apr 09 // was implemented in an R_count* sequence awhile ago, corrected here 12 May 09 // V.R_S_T.AddValue((R_count_save /100) + // max(V.R_S_T[]) already done in R_count* seq //in case was munged Rain_Season_total =max(V.R_S_T[]) // Remove Private 12 May 09 // this should give us number of missing readings add_lim =floor(((now_time -R_count_last_time) /360)) // all should be integers endif // end conditional have History 28 Apr 09 // Just in case logic screwy // but day_changed overrides 01 May 09 if ((add_lim +Day_changed) <1) return() endif // // NO ftp, but do midnite here 07 Mar 09 if (Day_changed !=0) // 27 Apr 09 rather than Todays_YYOday !=YYoDay) // add this to history 01 May 09 Mote1 ="Day change in `/ time" Note2 ="Clear Historys" beginexport(aHistory) delay(1) ? Note1 + ": doing " +Note2 // 29 Apr 09 clear_all_histories() // implement 28 Apr 09 // new nowtime if clear_all_histories took long time 08 May 09 now_time =floor(systime()) add_lim =floor((now_time -midnite) /360) // floor added 29 Apr 09 R_count_last_time =midnite R_day_inches =0 // clear this also 08 May 09 S_kw_hrs_save =0 // and this dp =0 // data points for "today" is zero endif // check if over 24 hours revised 07 Mar 09 // this should never happen, but be paranoid //while(add_lim >239) // add_limit =add_limit -239 // // adjust R_count last time also //endwhile // Just in case //if (add_lim <1) // return() //endif // Don't think need this 12 May 09 //R_count.AddValue(0) // so we don't double dip 11 Feb 09 // get our channel list AND chan_count for Real and Virtual GLOBAL vars // Global string channel_list =channel.ListAll() // ditto // Global String V_channel_list =V.channel.ListAll() // global chan_count =0 // global V_chan_count =0 // 11 Feb 09 chan_list() call NOW done in cold_start_new i.e., Autostart routine. // corrected closing paren on execute statements // private c_c =0 // channel loop counter private a_c =0 // add value counter // added one 24 Apr 09 private c_L =max((chan_count, V_chan_count)) +1 // most channels we have to do // add time strings 07 Mar 09 Private string add_val Private time_val =R_count_last_time //private add_L =0 // add this many values ? "adding " +doubletostr(add_lim) //v.test.AddValue(inserttime(NaN(),.Time[0],0)) Global string base_time Global string add_date_val // 24 Apr 09 corrected to string // revised outer loop to add values, rather than channel 07 Mar 09 // add value loop for (a_c =0, a_c <=add_lim, a_c++) // revised 02 May 09 base_time =DoubleToStr(time_val) // assign the time to use base_timef =time_val hr =FormatDateTime("%M", time_val) // the damn thing has to be quoted!!!!!!! and subtract a second 24 Apr 09 add_date_val ="'" +FormatDateTime("%m/%d/%y %H%M", (time_val -1)) +"'," // update our Hour files we hope 02 May 09 If (hr =="00") // delay(1) // xport_hour_stuff() // delay(1) ? add_date_val // debug do hr export here endif time_val =time_val +360 // increment for next time thru 02 May 09 for (c_c =0, c_c <=c_L, c_c++) // remove all R_date_time & V.date_time code that was commented out 02 May 09 add_val ="NaN()," if (c_c <=chan_count) execute(channel_list(c_c) +".addvalue(inserttime(" +add_val +base_time +",0))") endif // NOW virtual channels keep "nd" & R_S_T ???? if (c_c <=V_chan_count) // reinstate Date 08 May 09 if (V.channel_list(c_c) =="Date_time") add_val ="x" endif // try it 02 May 09 if (V_channel_list(c_c) =="nd") add_val ="'ND'," endif if (add_val !="x") // disable Date time assign 12 May 09 // ? "L 134 " +"v." +V_channel_list(c_c) +".addvalue(inserttime(NaN()," +base_time +",0))" execute("V."+V_channel_list(c_c) +".addvalue(inserttime(" +add_val +base_time +",0))") endif endif //***** end V chan if endfor //<<<<<<< end channel loop // debug ? c_c //<<<< end of add times loop endfor //<<< end add loop // add for insertTime( 28 Apr 09 Private fp_base_time =StrToDouble(base_time) // now have this many data points dp=dp +add_lim W_count.ClearHistory() // added (insertTime( // 28 Apr 09 w_count.AddValue(insertTime(0,fp_base_time,0)) w_count.AddValue(insertTime(0, fp_base_time,0)) // just clear the R_inches LJ counter /100 // 29 Apr 09 V.R_inches.AddValue(insertTime(0, fp_base_time,0)) // add Note1 ="`/ time end" Note2 =" dp & adds " +DoubleTostr(dp) +" " +DoubleToStr(add_lim) beginexport(aHistory) // Save more stuff 28 Apr 09 if (LJ_reset_done !=0) R_count_save =0 // use only if LJ_reset_done =0 endif // NOTE Times will be kewacky might want to revise??? // revised to insertTime 28 Apr 09 R_count.AddValue(inserttime(R_count_save, fp_base_time,0)) V.R_d_inches.AddValue(inserttime(R_day_inches, fp_base_time,0)) V.S_kw_hrs.AddValue(insertTime(S_kw_hrs_save,fp_base_time,0)) // end save more stuff 28 Apr 09 // add (insertTime( 28 Apr 09 V.R_S_T.AddValue(insertTime(Rain_Season_total, fp_base_time,0)) // restore this to TOP of stack The only way I can get nHum and nVsup channels to clear reliably is with straight code of: **** nVsup.ClearHistory() nhum.ClearHistory() *** Just ran the code again, and it cleared all histories. I'll keep you posted. ek Link to comment Share on other sites More sharing options...
AzeoTech Posted May 12, 2009 Share Posted May 12, 2009 Re max: it only worked because the bigger value was second. Try this: ? max((20,10)) it will return 10. Link to comment Share on other sites More sharing options...
ekanderson Posted May 13, 2009 Share Posted May 13, 2009 OK, forget max(). Main problem is clearing histories. Executed clear history code 3 times since my last post. 3 times did NOT clear the mentioned channels. Real channels 0 thru 11 supposededly executed. Any suggestions. Or should I just give up and hard code mychannel.clearHistory(). ek Link to comment Share on other sites More sharing options...
AzeoTech Posted May 13, 2009 Share Posted May 13, 2009 You've got something else going on. I'd need to see your .ctl doc. Link to comment Share on other sites More sharing options...
ekanderson Posted May 13, 2009 Share Posted May 13, 2009 File is for LJ U3 Lots of luck ek Link to comment Share on other sites More sharing options...
AzeoTech Posted May 13, 2009 Share Posted May 13, 2009 I actually don't see any problem. It worked just fine for me. That said, I also simplified the system. I turned off all your sequences (since they expected things like paths that I don't have), and set the channels to poll using Timing, and I was able to run the clear_all_histories sequence and have it clear out every time. Now I also eliminated all the delay()'s in that sequence, since they are not needed, and having it means that the sequence takes 50 seconds or so and during that time a bunch of data could reaccumulate (I had a timing of 1). Try simplifying it down on your end as well. PS: I'm on 5.80. On a different note: you have a user/password for your ftp on the doc. I have deleted the attached file so no one else gets access to it and I believe I'm the only one that downloaded it so you are safe, but be aware that you may want to change your ftp password just in case. Link to comment Share on other sites More sharing options...
ekanderson Posted May 14, 2009 Share Posted May 14, 2009 Damn, forgot all about the passwords. There are two, one in each Ftp_to_* The whole idea of this, was to get AWAY from timing as suggested by a guru at azeotech in order to totally control timing of data collection. In my code there is NO LJ i/o that I know of until well after the clearHistory sequence. It maybe due to the slow machine and 512Mbytes of memory I'm using as the development machine. However while that code is running, there are still some CPU ticks and memory available if we can believe TaskManager. Rest of program seems to work AOK. I am almost at the stage of porting it to the data collection machine, but wanted it thoroughly debugged so as to not interupt data collection. Am trying to solve a problem with NaN getting put out as 100000000000000000000 etc. to my data files and will be ready to port. The delays were inserted because the histories were not clearing and thought that might solve the problem. ek Link to comment Share on other sites More sharing options...
ekanderson Posted May 16, 2009 Share Posted May 16, 2009 The only way I've been able to get channel history's to clear is by erasing the Persist files BEFORE starting DF. NOTE: even if the *.ctl file is loaded in Safe Mode, the persist files are locked by DF, so must be done before loading the *.ctl file. ek Link to comment Share on other sites More sharing options...
ekanderson Posted May 16, 2009 Share Posted May 16, 2009 *.ctl file xfred to the fast machine. clearHistory() on fast machine also has problems IF there are Persist data files for the channels. Only way I can reliably get ALL histories to clear.. Before loading DF *.ctl file, erase all Persist files. Then execute DF *.ctl file. Odd note: DF saves my *.ctl file with histories, even when just "save" is selected under "file". Link to comment Share on other sites More sharing options...