andybdjuk Posted June 3, 2009 Share Posted June 3, 2009 Hi Guru, I am messing about with a flowmeter that has 130 Pulses/Litre. Can you give me some help to read in the pulses and display in L/min. At the moment I am not getting credible values. Thanks Andy Link to comment Share on other sites More sharing options...
AzeoTech Posted June 3, 2009 Share Posted June 3, 2009 I can't really help with the input itself. You'll need to talk with the DAQ hardware manufacturer about why your values don't make sense. However, to convert from pulses/litre to L/min I can help you. I'm going to assume that you are using a counter and that your are not resetting the counter between reads, so it is simply counting up. You'll need to create a second Test channel to hold the result. Timing = 0, Type D to A, but the rest doesn't really matter. Then in the Event of your RawCount channel, put: FlowRate = ((RawCount[0] - RawCount[1]) / (RawCount.Time[0] - RawCount.Time[1]))/130*60 The bulk of it is simply giving you pulses per second since [0] - [1] is pulses in the interval, and .time[0] - .time[1] is the length of the interval. So: pulses/sec * 1/130 litre/pulse = litre/sec * 60 sec/min = litre/min Link to comment Share on other sites More sharing options...
andybdjuk Posted June 7, 2009 Author Share Posted June 7, 2009 Thanks Guru it works perfectly. Link to comment Share on other sites More sharing options...