klimas Posted December 27, 2009 Share Posted December 27, 2009 Hi, don Link to comment Share on other sites More sharing options...
AzeoTech Posted December 28, 2009 Share Posted December 28, 2009 Is it plugged into your serial (RS232) port? Or is it just a serial 1-wire plugged into an adapter into USB or something? If the first (I doubt it), you'd need to know the protocol and if your 1-wire to 232 converter is doing anything besides hardware translation. If the second, then you need to get the DLL provided with the adapter and access it using the extern() function. I know that others have successfully done this with little effort. Link to comment Share on other sites More sharing options...
klimas Posted December 31, 2009 Author Share Posted December 31, 2009 Hi, thanks for reply. It is 1-wire thermometer connected via com port adapter 9097. ARE THERE THEN THOSE "OTHERS" WHICH WERE SUCCESFUL AND CAN GIVE ME A HINT? Thanks!!! Link to comment Share on other sites More sharing options...
AzeoTech Posted January 7, 2010 Share Posted January 7, 2010 Post the docs, or a link to the docs for that adapter if you can. Link to comment Share on other sites More sharing options...
klimas Posted January 25, 2010 Author Share Posted January 25, 2010 Thanks for reply, it should be here: http://www.maxim-ic.com/quick_view2.cfm/qv_pk/2983/t/do and here http://www.maxim-ic.com/products/ibutton/s...re/sdk/sdks.cfm Link to comment Share on other sites More sharing options...
RJE Posted March 11, 2010 Share Posted March 11, 2010 Any luck with 1-wire comm's #63? This was going to be my next little project for DF but after reading over maxim's literature I doubt I could do it without some help. I did set up a 4 18S20 temp sensor network to the serial adapter and maxim's Java program sees them all and gets the temp values from them but there is no way to log the temps. RJE Link to comment Share on other sites More sharing options...
RJE Posted March 24, 2010 Share Posted March 24, 2010 This is just some preliminary info on the DS18S20 1-wire temp sensor that I have learned so far. It doesn't seem to be as bad as I thought. This unit is being replaced with the DS18B20 temp sensor but I have 10 of the 18S20 sensors that I would like to use with DF. My network will be powered (not parasite power) and use the serial adapter DS9097U which takes commands from the serial port and then out to the 1-wire network. I believe this unit has the DS2480B 1-wire driver chip in it, so called the master. Each DS18S20 temp sensor has a unique 64 bit rom ID that is used for addressing each one on the 1-wire bus. I used Maxim's Java app to get the rom id of each of my sensors so this way I don't have to clutter my DF script with rom searching etc. One of my sensors has a rom ID of $10, $03, $88, $6B, $01, $08, $00, $4A. Operation as I understand it right now: Tx $C1 send reset command, puts all 1-wire units into idle Rx $CD this is the presence response meaning there are devices listening Tx $55 send match rom ID command to master - looking for specific sensor Tx send the sensors rom ID Tx $44 send convert temp command to the selected sensor wait for conversion (time unknown right now) Tx $C1 reset command Rx $CD presence response Tx $55 send match rom ID command to master Tx send the sensors rom ID Tx $BE send read sensorsscratch memory Rx 9 bytes back The first eight bytes are temp info and the ninth byte back is the CRC of the first 8 with which the master uses to check if the data is good. The scratch memory map of the DS18S20 is: 0 - Temp LSB 1 - Temp MSB 2 - Th register 3 - Tl register 4 - Reserved 5 - Reserved 6 - Count Remain 7 - Count per deg C 8 - CRC Using the Count Remain and Count per deg C values in the temp calcs you can increase your resolution but I haven't gotten that far yet. I'll carry on and let you know how things progress. RJE Link to comment Share on other sites More sharing options...
RJE Posted March 31, 2010 Share Posted March 31, 2010 Well things are never easy are they? The commands are spread across several of the 1-wire documents and that makes it difficult to figure things out. So far I'm up to starting the conversion process in the temp sensor (I think). After the start conversion command I have to send the command for "read time slots", this command tells the master to do its work with the one wire bus to get the done command back from the sensor. The Rx byte will have bit 0 set to 0 if not done and set to 1 if done, all other bits are 'don't care'. This is where I always get confused, what to do with the Rx byte. My basic loop is this. device.one_wire.Write(chr(0x44)) //start conversion command delay(1) //wait for conversion private stat = 0 private resp while (stat == 0) device.one_wire.Purge() device.one_wire.Write(chr(0x95)) delay(0.1) private data = device.one_wire.Read(1) resp = to.uByte(data) stat = (resp && 1) endwhile The Comm window shows I'm getting 97 back but my loop just keeps looping. Where am I going wrong? RJE Link to comment Share on other sites More sharing options...
AzeoTech Posted April 1, 2010 Share Posted April 1, 2010 First, && is a boolean AND. I think you want & which is the bitwise AND. Second, you can use asc() intead of to.uByte() Other than that, I don't see anything. Try either adding some debug ? statements (of the contents of resp and stat), or just step through the code using the debugger and look at these directly. Link to comment Share on other sites More sharing options...
RJE Posted April 3, 2010 Share Posted April 3, 2010 Well it's crude and rude and maybe socially unacceptable but it works. The 1-wire sensor matches my calibrated Fluke meter with its temperature probe. private alive private tempL private tempH private regH private regL private res1 private res2 private CR private CP device.one_wire.Purge() device.one_wire.Write(chr(0xE3)) //set master to COMMAND MODE device.one_wire.write(chr(0xC1)) //send MASTER RESET delay(0.1) device.one_wire.Write(chr(0xE1)) //set master to DATA MODE alive = device.one_wire.Read(1) //0xCD returned will indicate devices on the bus (nothing done with this yet) device.one_wire.write(chr(0x55)) //send match ROM command device.one_wire.write(chr(0x10)) //send specific device ROM id device.one_wire.write(chr(0xD3)) device.one_wire.write(chr(0x88)) device.one_wire.write(chr(0x6B)) device.one_wire.write(chr(0x01)) device.one_wire.write(chr(0x08)) device.one_wire.write(chr(0x00)) device.one_wire.write(chr(0x4A)) delay(0.1) device.one_wire.Write(chr(0x44)) //send start conversion command delay(1) //wait for conversion usually 0.75 secs private stat = 0 private resp while (stat == 0) //send read time slots until bit0 = 1 which means conversion done device.one_wire.Purge() device.one_wire.Write(chr(0x95)) delay(0.1) private string data = device.one_wire.Read(1) resp = asc(data) stat = (resp & 1) endwhile device.one_wire.Write(chr(0xE3)) //set master to COMMAND MODE device.one_wire.Write(chr(0xC1)) //send MASTER RESET command delay(0.1) device.one_wire.Write(chr(0xE1)) //set master to DATA MODE alive = device.one_wire.Read(1) //0xCD returned will indicate devices on the bus device.one_wire.Write(chr(0x55)) //send match ROM command device.one_wire.Write(chr(0x10)) device.one_wire.write(chr(0xD3)) device.one_wire.write(chr(0x88)) device.one_wire.write(chr(0x6B)) device.one_wire.write(chr(0x01)) device.one_wire.write(chr(0x08)) device.one_wire.write(chr(0x00)) device.one_wire.write(chr(0x4A)) delay(0.1) device.one_wire.write(chr(0xBE)) //send master READ SCRATCH PAD command device.one_wire.Purge() //send write time slots to get device conversion data device.one_wire.Write(chr(0xFF)) delay(0.1) private string firstdata = device.one_wire.Read(2) //for some reason 0xBE is echoed back first then data device.one_wire.Purge() device.one_wire.Write(chr(0xFF)) delay(0.1) private string byte2 = device.one_wire.Read(1) device.one_wire.Purge() device.one_wire.Write(chr(0xFF)) delay(0.1) private string byte3 = device.one_wire.Read(1) device.one_wire.Purge() device.one_wire.Write(chr(0xFF)) delay(0.1) private string byte4 = device.one_wire.Read(1) device.one_wire.Purge() device.one_wire.Write(chr(0xFF)) delay(0.1) private string byte5 = device.one_wire.Read(1) device.one_wire.Purge() device.one_wire.Write(chr(0xFF)) delay(0.1) private string byte6 = device.one_wire.Read(1) device.one_wire.Purge() device.one_wire.Write(chr(0xFF)) delay(0.1) private string byte7 = device.one_wire.Read(1) device.one_wire.Purge() device.one_wire.Write(chr(0xFF)) delay(0.1) private string byte8 = device.one_wire.Read(1) private string byte1 = Right(firstdata,1) //get rid of first byte that's echoed back tempL = asc(byte1) tempH = asc(byte2) regH = asc(byte3) regL = asc(byte4) res1 = asc(byte5) res2 = asc(byte6) CR = asc(byte7) CP = asc(byte8) private count = (16 - CR) / 16 //calc temp using higher resolution method private temp = (tempL / 2) - 0.25 + count Temp_1.AddValue(temp) Now on to adding more sensors to the 1-wire bus. There is no error detection or anything so user beware and you must know the ROM ID of the sensor you want data from. RJE Link to comment Share on other sites More sharing options...
AzeoTech Posted April 3, 2010 Share Posted April 3, 2010 You can probably replace the long chain of write() with a single write. Ie, this: device.one_wire.write(chr(0x10)) //send specific device ROM id device.one_wire.write(chr(0xD3)) device.one_wire.write(chr(0x88)) device.one_wire.write(chr(0x6B)) device.one_wire.write(chr(0x01)) device.one_wire.write(chr(0x08)) device.one_wire.write(chr(0x00)) device.one_wire.write(chr(0x4A)) to this: device.one_wire.write(chra({0x10,0xD3,0x88,0x6B,0x01,0x08,0x00,0x4A})) Link to comment Share on other sites More sharing options...
RJE Posted April 8, 2010 Share Posted April 8, 2010 Hi Yes I know but since each device's ROM id will be in the script I thought this would be easier to make sure I entered it right. One thing I haven't figured out yet is the docs say the data back is in 2's compliment form but the MS byte back of the 2 bytes back is the sign. See the attached pic. Still have to figure this out for the outdoor temp sensors. I'm waiting for delivery of my 6 channel master 1-wire hub to arrive so that I can start adding multiple sensors. Working on the DS2438 chip which has a 0 - 10V AD input plus a current sense input, this will be used to get the humidity values from my Honeywell sensors. Onward we shall go! RJE Link to comment Share on other sites More sharing options...
AzeoTech Posted April 8, 2010 Share Posted April 8, 2010 The docs are just being confusing. They are saying the upper byte is all sign, when really they are just using a signed word value to represent their values. The upper byte presumably is always either 0 or 0xff because the sensor never goes above 127C or below -127C. Just treat the incoming value as a signed word (use the To. and From. functions) and it should come out right. Don't forget to divide by 2. Link to comment Share on other sites More sharing options...