polilies Posted April 6, 2010 Share Posted April 6, 2010 Hi Azeotech team; I'm trying to communicate with a "Delta" inverter. Few days ago i able to read the curent values of inverter. i used "read holding u16 (3)" I/O type . But when i tried to write in it there is a problem about it. In I/O type list i can't find "Set Register U16 (6)" . Instead of it, ı used the "Set Register U16 (6)" I/O type , it writes! but for writing i have to send upper value then a hundred. for example i sended "20090" it appears in the display like this "200.9". and it didn't accept lower then hundred values. can you help me about it? thank you so much from now. nice day Link to comment Share on other sites More sharing options...
AzeoTech Posted April 8, 2010 Share Posted April 8, 2010 I'm sorry I don't completely understand. Do you want the display to show 200.9 but actually send the value 20090 to the register? If so, create a conversion: Value * 100 and apply it to the output channel. Link to comment Share on other sites More sharing options...