MODBUS TCP SLAVE PROBLEM


RMV

Recommended Posts

If what you attached is the Rx from the iFIx, then the issue is that it is requesting from Modbus ID 0. ID 0 is reserved (by the Modbus Protocol) for broadcast messages. You should use Modbus ID 1. Also, note that you are using command 1, and really should be using command 3 or 4.

Link to comment