Reading greater then 20 register at once


polilies

Recommended Posts

Hi, i'm trying to read registers from an "analizor" which the registers starting from 0000h address. And i'm

using "readholdingU16" function to read multi register at once but what i get is only 20 registers value. So is

there a limitation about this stuation? is the limit 20 for "readholdingU16" function? Cause when i try this via

another program i can get datas more then 20. thank you so much.

Link to comment
Share on other sites

There is a limit defined by Modbus, but its not 20. It varies depending on TCP vs RTU. I'm guessing you are displaying the result in a variable value control? This control only displays the first 20 elements of an array, so this is likely why you are only seeing 20 values.

Note that you can create separate channels for all your registers, and provided they are sequential and have the same timing/offset and I/O type, DAQFactory will automatically combine them into a single read.

Link to comment
Share on other sites

  • 3 weeks later...

thank you so much for your answer. now i can see it.

i need to ask something but i can't sure should i write this to a new toic?

İ need to use DAQ as a modbus TCP slave and i want to read multiple registers from DAQ. is making the

register adresses serial enough to read them?(more than one)

Link to comment