I persistantly receive the following message in the Command/Alert window

C1038 Timing Lag, data acquisition stalled. Resetting Timing: 1.000, Offset: 0.000

I have 10 analog input channels set at: Timing 1.00 Offset: 0.00

I have a further 9 channels reading values from a modbus gateway set at: Timing 10.00 Offset 0.00

the reason for the modbus gateway timing setting is that the gateway updates the gateway register data at 10 second intervals.

Currently the C1038 messages appear about every 3 minutes.

I have tried everything I can think of to isolate the problem - but am at a loss now how to proceed any further.

Any thoughts ?

PS - my ctl file is too large to upload.

Link to comment
Share on other sites

Timing lag means that the system was not able to keep up with the desired polling rate. In your case, its with the channels with Timing = 1. Apparently it is taking slightly longer than 1 second to poll all 10 input channels. To eliminate this error you'll either need to decrease your polling rate (increase Timing), or figure out how to make your hardware faster, for example by blocking your tags if that is an option.

Link to comment
Share on other sites

I assume that by "blocking your tags" you mean the DAQConnect tags ?

If not - what do you mean ?

Link to comment
Share on other sites

No, DAQConnect has nothing to do with it.

By blocking your tags I am referring to Modbus. I don't know what you are using, but if you are using Modbus and you can arrange your tags so that they are in order (i.e. channel #1, 2, 3, etc for U16/S16), then DAQFactory can make one query instead of multiple queries which is much faster.

Link to comment
Share on other sites

Ok - My Modbus configuration in the order thay appear in the channel table is as follows: n.b. all having timing set at 2.00

TAG I/O Type Chn#

V01_degC Read Holding S16(3) 6

V02b_m_s All others: Read Holding U16(3) 8

V02_m_s 7

V03_deg 9

V04_R_mm 28

V05_ET_mm 31

V06_RH 18

V07_hPa 3

V08_IR 25

V09_mm 23

Link to comment
Share on other sites

The order in the table doesn't matter. If you can make deg_C U16, it will help slightly, but then you won't be able to measure below 0C presumably. As for the rest, do you have any control over the locations? If so, move them so they are all in a block. If not, consider adding some dummy channels for at least 24,26,27,29 and 30 and maybe even 19,20,21 and 22. Just call them dummy24, dummy26, etc. or whatever you want. You don't have to do anything with them, but by telling DF you want to read those channels, DF can make a single query for channel 18, requesting 14 registers. Right now, reading those tags above 18 takes 5 different requests. Do the same at the low end, especially if you make degC U16 (or make the others S16? I don't you'll overflow 15 bits for those tags unless there is a scaling factor). That'd mean adding dummy tag 4 and 5. Then you'd be down to two requests to read all your tags instead of the current 8 requests.

Link to comment
Share on other sites

THnaks for that ...

I don't really need to read below 0 degC so I can change that tag to U16 and leave all others at U16 as well.

I see what you mean with the dummy tags. DF can read them but I don't necessarily need to do anything with the data.

Link to comment
Share on other sites

Thankyou ...

That seems to have solved those issues.

Now have one other problem.

I regularly keep getting:

D0050:01:1008 LabJack Device #1 error: Communications failure

Sometimes it is LabJack 2 (I'm using 2 LabJacks using wifi) ?

Link to comment
Share on other sites

I think I've solved my comms failure alert - seems that my wifi signal is low and packet losses might account for the issue - relocating the wifi repeater for better signal strength appears to resolve that problem