Write To Register Unsigned 16 Modbus Tcp


SALICIS

Recommended Posts

Hi,

Excuse me for my poor english.

I communicate with power station with Azeotech. No problem for read register but i don't write!!

I would like to write to 16 bits unsigned register, but I don't find a command. There isn't setregisterU16(...).

In the Help i don't find  description of modbus TCP functions....the difference between Readholdingregister, readregister....

 

Thank you for your help

Link to comment
Share on other sites

That's because they actually are the same when it comes to output.  That is perhaps confusing, but you will find that if you select Set Register (S16), and you try to set a value, such as 65000, you will actually get the correct output.

 

I've changed the files to be more clear in the next release.