Rorrog Posted June 10, 2023 Posted June 10, 2023 I am started in this, I usually schedule with PLCs, and I need to make a pulse counter block, but I fail to define the variable with a rise or decrease flank. example: Var.count_1 = 0 Var.count_2 = 0 Var.Habilitacion = 0 while(1) If (Var.habilitacion >= 1) Var.count_2 = Var.count_2 + Var.count_1 Endif Endwhile When var.counter_1 is 1, the application does not count from 1 in one if not in several numbers with respect to the PC scan. The difference in the application that will use an input as an accountant instead of a variable. Var.count_1 = CO_0 for exaple. Thanks for the attencion. Quote
AzeoTech Posted June 12, 2023 Posted June 12, 2023 A couple things: 1) I recommend against using var. notation. This is left over from very old ( > 15 years) releases of DAQFactory. Instead use variable declaration. So: global count_1 = 0 global count_2 = 0 global habilitacion = 0 while(1) if (habilitacion >= 1) count_2 = count_2 + count_1 endif endwhile 2) you have an infinite while() loop without any delay. This script will use a lot of CPU power, most of which will be wasted. I suggest adding at least a delay(0.01) before the endwhile. As for the rest, the script looks fine. It will loop forever and whenever habilitacion >=0, it will increment count_2 by count_1. Quote