Command / Alert Message


ahmedaboueid88

Recommended Posts

Hi everyone,

 

I have the daqfactory software connected to PLC FATEC to control a blow moulding plastic machine, but the program is not working and an alert message appears in the cammand / alert tape which is " unable to load device driver DSXMODBUS.dll, check file path and make sure manufacturer's drivers are installed ". What should I do to get the program working and connected to the PLC?

 

thank you for any help

Link to comment
Share on other sites

Are you trying to talk Modbus to the device?  If so, you need to use "New Serial/Ethernet device" to create a modbus connection.  DSXModbus.dll is an old modbus driver from many years ago.  There is a guided tour on using Modbus included in the installation.  It is in the DAQFactory folder of the Windows Start menu. 